Dear teachers, here is a calculation sheet for the orifice plate flow meter. By how much should the range of the pressure difference transmitter and the DCS be adjusted?
Reply #22020-03-22
Pressure difference: 6 kPa, DCS flow rate: 80,000 Nm3/h
Reply #32020-03-22
Then take the square root of the pressure difference transmitter?
Reply #42020-03-23
You can take the square root at the transmitter or at the DCS; you just need to remember that 4 mA equals 0 and 20 mA equals 80,000. Thinking too much will only make things more confusing. . .
Reply #52020-03-23
The differential pressure transmitter has a range of 8 KPA; the value in DCS is 80,000 standard cubic units. It’s simplest to take the square root on the gauge, without having to fiddle with it in the DCS.:D
Reply #62020-03-23
Differential pressure: 6 kPa; range: 80,000 bar. The square root value is the same whether it is calculated on-site or in the system. It seems to be a gas; pay attention to whether there is any compensation.
Reply #72020-03-24
The range of the 0-6kpa gauge is 0-80000 as configured in the DCS

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.