What is an alarm dead zone?

2020-03-22View Original

Thread Content

Could someone explain it simply? I’ve searched for some answers, but I still don’t understand
Reply #22020-03-22
This post was last edited by jlshnlhj on 2020-3-23 at 10:28. To put it this way, the pressure is in the range of 0–1.5 MPa, with an alarm triggered at 1 MPa. Normally, when PV ≤ 1 MPa, the alarm should be cleared; however, sometimes the process isn’t yet stable, and PV keeps fluctuating around 1 MPa, causing the alarm system to continue issuing alerts. To prevent such a situation, the threshold for exiting the system alarm state is set at 1 range * 2% (it can also be set to 2%-5%) MPa, that is, 0.97 MPa; this means that when PV

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.