Coverage radius of the oxygen detector

2020-07-08View Original

Thread Content

May I ask about the coverage radius of the oxygen detector? GBT50493 does not specify this clearly; it only recommends the use of electrochemical detectors. Does that mean we should proceed based on the radius associated with toxicity?
Reply #22020-07-15
This post was last edited by Bi Ren on 2020-8-5 at 13:41, with the latest version of GBT 50493-2019 – Design Code for Detection and Alarm of Flammable and Toxic Gases in Petrochemical Industries attached
Reply #32020-08-05
Is there no one in the instrumentation and automation department?
Reply #42020-08-06
For toxic gases, the distance between two gas detectors should be no more than 4 meters. But standard construction practices usually designate specific areas for this purpose; otherwise, the specifications would require a fixture to be installed every four meters throughout the entire room. The new standard is currently recommended rather than being mandatory – it seems that it’s not required by law, and it’s sufficient for the designers and builders to reach an agreement together.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.