Help needed with ASCO solenoid valve! ! ! Urgent! !

2020-10-28View Original

Thread Content

As shown in the diagram, why is air leaking from port 3 when the solenoid valve is not powered?
Reply #22020-10-28
The gas source inlet is connected incorrectly; it seems that 2 is the inlet, 1 is the outlet, and 3 is the exhaust port. When there is no electricity supply, 1 and 3 remain open. Check whether 1 has been mistaken for the inlet, or simply blow air into port 1 or 2. If air comes out of port 3, then it’s the outlet of the solenoid valve
Reply #32020-10-30
It’s either the seal is damaged or there’s dirt on it. Open it up and you'll see.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.