Problems with the setup of radar level transmitters

2020-10-29View Original

Thread Content

I have 10 tanks here, and the level gauges on top of these tanks are used ones; the brand is from Cologne, Germany, and the model is OPTIFLEX1300C-L. I’ve entered the height of the tanks, as well as the height and diameter of the waveguide, but why isn’t the display reading zero? The tanks are empty, so I’m not sure what’s going on. Please advise me, experts.
Reply #22020-10-29
Calculate and re-enter the height of the waveguide. What is the radar’s dead zone? Is the waveguide installed vertically correctly? If it is installed properly and set up correctly, a reading that is not exactly zero is acceptable. If the deviation is large, there is a problem with the installation or your settings.
Reply #32020-10-30
After I made the settings, the display on the gauge showed values such as 0.01m, 0.02m, and so on, but none of them were zero.
Reply #42020-10-30
This should work. If you want it to be 0, you can reduce the waveguide value by 0.01, or adjust it by measuring the height
Reply #52020-10-30
Such a small value can be considered a measurement error; let’s transfer it from the instrument side or the DCS side.
Reply #62020-10-30
At least give it some margin of error, will you?
Reply #72020-11-04
The display on the liquid level transmitter at the site shows 0.086 m, while the DCS shows 0.000 m. Why is this?
Reply #82020-11-05
Almost there – where did you get the tank height data you entered? When the tank is empty, the radar can measure its height on its own, and the measurement taken by the radar is more accurate.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.