Are there any specified standards regarding the number of voting options for chemical process interlock sensors, such as three-out-of-two or two-out-of-two?

2021-01-08View Original

Thread Content

Are there any specified standards regarding the number of voting options for chemical process interlock sensors, such as three-out-of-two or two-out-of-two? We only do individual pickups here; we want to have standards that are more convincing.
Reply #22021-01-08
In the case of a DCS system, the importance of the process is the key factor to consider. If the consequences of a shutdown due to faults in the channels or instruments are severe, such as significant financial losses, a 3-out-of-2 configuration can be used, as the additional cost of instruments is relatively lower compared to the cost of a shutdown. While a 2-out-of-2 configuration improves reliability, it reduces safety; therefore, a good strategy is needed to prevent failures in operation
Reply #32021-01-08
Hardware Margin.png If it meets the requirements in the SIS reference image

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.