When measuring pressure or differential pressure, and depending on how the three (two, five) valve assemblies are installed, is it still necessary to add a stop valve? Are there any guidelines I can refer to?
Reply #22021-02-03
Standards stem from principles; as long as the principles are feasible and safe. It would be best to send a diagram of the three (two, five) valve assemblies, so I can see what they look like. Thank you!
Reply #32021-02-03
A primary valve near one end of the equipment pipeline is still needed. It’s not necessary on the side closest to the transmitter; after all, the valve assembly is designed to replace the function of several valves.
Reply #42021-02-03
There are two-valve assemblies, three-valve assemblies, five-valve assemblies, etc. . = =、
Reply #52021-02-03
It's definitely a good idea to install a shut-off valve on the equipment side. Are there any recommended standards that can be followed regarding the use of this valve assembly and the shut-off valve?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.