Calibration of diaphragm-type double-flange differential pressure level gauge

2021-03-23View Original

Thread Content

A tank is equipped with three level gauges, A, B, and C. The height of the tank is 2 meters, and the density of the medium inside it is 1.15. The levels of liquids in gauges A and B are at 60%. C is a double-flange differential pressure level gauge. The header shows that the liquid level is 58%, assuming the pressure is 12 KPA. How to set the liquid level of liquid C to 60%? What are the calculation steps? Silicone oil density: 0.9
Reply #22021-03-24
Using Δp=ρgh, the calculated differential pressure range is 22.54 Kpa. If the current pressure is 12 Kpa and 58% is displayed, and without considering the issue of scale shift, the range is set at 0–22.54 Kpa. To achieve a reading of 60%, the calculations are as follows: 1. 22.54 (range) * 60% = 13.524 Kpa – this is the pressure required for a 60% display. 2. 12 (current pressure) – 13.524 (required pressure) = -1.524 Kpa; this indicates that the range needs to be adjusted downward by 1.524 Kpa, to the range of -1.524–21.016 Kpa.
Reply #32021-03-24
Furthermore, there is a problem with your question itself: if the three level gauges use different measurement methods, it’s normal for discrepancies to occur (for example, with radar or ultrasonic level gauges). If the range of the double-flange transmitter is adjusted arbitrarily, it will also give inaccurate readings in other locations. 2. Are the measurement ranges of 2 or 3 gauges the same? If not, the measurements will also be inaccurate.
Reply #42021-03-24
What I really want to say is that I would like to know the calculation process. Thank you

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.