The positive and negative pressure measurements of Honeywell’s differential pressure transmitter are reversed; can this be corrected using the handheld controller?

2021-10-16View Original

Thread Content

The positive and negative pressure measurements of Honeywell’s differential pressure transmitter are reversed. Since it’s a high-pressure flange of 1500 pounds, replacing the gaskets would require too much work; is it possible to adjust this setting using the handheld controller? The model should be STD700.
Reply #22021-10-16
It depends on what your range is and whether it meets the requirements; if the range is small, it’s usually sufficient
Reply #32021-10-18
Yes, but the DCS zero point and range need to be set accordingly during configuration

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.