Flow meter selection

2017-11-01View Original

Thread Content

We plan to purchase a flow meter. Its main purpose is to measure steam flow for use in trade settlements. Note: Our unit does not have enough steam, so we intend to connect a steam pipeline from another company to supply steam for our production needs. The main parameters are as follows: Medium: superheated steam; Operating pressure: 1.3 MPa; Medium temperature: 225 degrees Celsius; Operating flow rate range: 0–30 T/h; Normal flow rate: 25 T/h; Pipe diameter: DN200; Installation orientation: horizontal; Accuracy class: not less than 0.5 class. What type of flow meter is suitable for use? I would appreciate it if experts could help. Additionally, our company plans to use imported mass flow meters, either from Emerson or E+H. I wonder if this is an appropriate choice; what is the approximate price range? Please let me know as well.
Reply #22017-11-01
Bar-type flowmeters work fine, whether it’s Delta Bar or Anubar. A high-temperature vortex flow meter can also be chosen; if higher accuracy is required, then a mass flow meter is the option
Reply #32017-11-01
To achieve such high precision, it is best to use a mass flow meter....
Reply #42017-11-01
Quality? MY GOD! It’s still a nozzle or a venturi.
Reply #52017-11-01
E+H is definitely out of the question – it has such a large diameter and also operates at relatively high temperatures. Ask Emerson
Reply #62017-11-01
For levels above 0.5, it is best to choose a mass flow meter.
Reply #72017-11-01
When using vortex street sensors, a necking is definitely required. Only a mass flow meter can achieve the accuracy you need, and it may not even be sufficient in practice.
Reply #82017-11-02
There should be ones from E+H, but it’s likely they won’t want to invest in imported mass flow meters either
Reply #92017-11-02
Mass flow meters have high precision but are expensive; there’s no need to use them for measuring steam
Reply #102017-11-02
Why does the vortex flow meter need a reduced diameter? There are also vortex flow meters with a DN200 size
Reply #112017-11-02
Why does the vortex flow meter need a reduced diameter? There are also vortex flow meters with a DN200 size

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.