What type of control valve should be used for steam control?

2021-10-20View Original

Thread Content

This post was last edited by liu530014416 on 2021-10-20 at 20:07. Operating parameters: 20 bar of steam before the valve, 10 bar of steam after the valve; normal steam flow rate is 27 t/h, steam density is 0.8, and the temperature ranges from 195 to 220 degrees. Question: What diameter should be chosen? What is the CV value? What type of valve should be used?
Reply #22021-10-21
Go and ask those manufacturers of valve systems for power plants; they are very professional
Reply #32021-10-22
DN250: CV value of 380 selected; calculated CV value is 139.995. The selection is based on this CV value; at an opening of 27 T/h, the percentage is 74.47%. Sleeve valve, material: WCB/316+ST/316+ST; extended valve cover; graphite packing
Reply #42021-10-23
A sleeve control valve with two-stage noise reduction is sufficient; a DN200 diameter is appropriate. The following are the results obtained using the company’s selection software
Reply #52021-10-28
Heating companies – they’re the best at this
Reply #62021-10-28
This post was last edited by The camellias remain as before on 2021-10-28 at 13:11
Reply #72021-10-28
Up to 220 degrees – it’s not considered a high-temperature valve. Why use a valve cover with radiators when a regular one will do just fine?
Reply #82021-10-28
This post was last edited by The magnolias are still there on 2021-10-28 at 13:16. The use of sleeve valves is for reference only
Reply #92021-11-02
Any valve supplier can provide you with these parameters; for steam applications, it’s best to use sleeve valves with a heat-dissipating type of valve cover
Reply #102021-11-16
For standard cage structures–if there is noise, one or multiple levels of noise reduction are available; detailed technical support can be provided

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.