Setting of the toxic gas alarm threshold for bromine gas

2022-01-12View Original

Thread Content

Dear seniors, how should the alarm threshold for bromine, a toxic gas, be set? I calculated using the formula provided in specification 50493; the threshold value for level 1 alarm is: 0.045 ppm ; The secondary alarm value is: 0.09 ppm. I’m not sure if it’s right or not
Reply #22022-01-12
How did you calculate it? According to the table, 0.3 mg/m3 should translate to 0.084, right? But there is also a corrigendum for 50493 itself:
Reply #32022-01-12
Your correction sheet is correct, but the “meeting minutes” listed on it seem to be invalid, right? Although no company wants to do this, the scope is too large

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.