Thread Content
It’s far from the control room; I want to place the IO cabinet on-site. Is there a way to do that? Can it be done? There is no cabinet room on site; the cabinets are simply placed there for wiring, with communications sent back to the control room. Is that acceptable?
It is feasible from a technical perspective, but it’s not clear whether there are any regulatory requirements
Explosion-proof, difficult to maintain and repair; cabinet temperature and humidity cannot be monitored
1. The cabinet must meet explosion-proof requirements; 2. Typically, PLCI/O cards can meet the requirements of field environments, while DCS cannot.
I don’t know where you mean by the scene Is it in an environment with explosion hazards? That’s not acceptable. It is completely feasible in on-site cabinet rooms that are not in explosive hazard areas. In fact, this is the case for all large-scale petrochemical plants at present. Connected to the central control room via fiber optic communication.
It is feasible both technically and in terms of standards.
This issue has been discussed many times on forums; from a technical and standard perspective, there are no problems. The potential issue now lies with the local safety supervision authorities. If the safety review is passed, then there should be no problems, though the situation varies from region to region.
As long as the explosion-proof rating of the explosion-proof cabinet meets the requirements, there should be no problem. But has it been considered that opening it when maintenance is needed would constitute illegal operation?
In explosive hazard environments, flameproof IO cabinets can be used, but opening them for maintenance is not permitted.