Is there any length requirement for the instrument air duct from the air source distributor to the valve?

2022-05-29View Original

Thread Content

This post was last edited by In Search of Forgotten Dreams on 2022-5-29 at 16:43. Which standard specifies the length requirements for the ducts running from the air source distributor to the valves? The design drawings do not specify the length; I would appreciate it if fellow sailors could help answer this question
Reply #22022-05-29
No requirements are specified in the standards. However, each valve manufacturer has practical requirements; generally, they require that the small-diameter section of the distributor not be longer than 10–15 meters, otherwise it will affect the performance of the valves.
Reply #32022-05-30
There are no specific restrictions, but the shorter it is, the better. If your gauge is connected via a thin tube to a location 10,000 kilometers away, just imagine how high the pressure in the gas supply would need to be, as well as the amount of time delay that would occur
Reply #42022-05-31
There are indeed no specific requirements for this, but everything still needs to be reasonable. First of all, the pressure at the valve must be ensured; generally speaking, the pressure of the air supply is fixed and cannot be adjusted arbitrarily, so it’s naturally not possible to have a very long distance between them. Usually, 10 to 20 meters is sufficient; if it’s longer, larger pipes need to be considered, or a gas storage tank can be added.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.