2024-04-01View Original

Thread Content

I’ve encountered a problem recently: one of the turbine flowmeters appears to be functioning properly on-site, but after operating for some time it occasionally shows values on the DCS system that remain fixed as if it has crashed; the normal operation is restored each time the power is cut off. One flow meter has been replaced, the channels of the DCS cards have been changed, and the cables have also been replaced, but the problem still persists. All other tests show no issues; it’s only this one device that has problems. What could be the reason for this?
Reply #22024-04-01
It might be a software issue with the DCS system, or a mismatch in communication protocols, resulting in unstable data transmission. It is recommended to check the software settings of the DCS system to verify that the communication protocol is properly matched to the turbine flowmeter, and to ensure that there are no interference signals affecting the communication. If both the software and communication protocols are fine, it may be necessary to contact the equipment supplier to check whether there is an intermittent fault with the flow meter itself. .
Reply #32024-04-01
The information you provided isn’t very sufficient; are you sure it’s not a vortex flow meter? How many wires does the flow meter have? What signals to DCS (communication, 4~20mA, frequency/pulse)?
Reply #42024-04-02
There should be no problem with the software; I contacted the DCS manufacturer, and other flowmeters don’t have this issue. Currently, it is mainly suspected that there is a problem with the 4-20mA output circuit of the flow meter, or rather, interference is the cause
Reply #52024-04-07
May I ask, regarding the issue you described, are the values shown on the local instruments consistent with those in the DCS? My advice is to identify the problem step by step
Reply #62024-04-07
Check whether the signal cable of this flow meter is placed together with the power cable; everything that needed to be replaced has been replaced, so the possibility of interference is very high. (Especially motor power cables with variable frequency)
Reply #72024-09-25
How was this problem resolved later on?
Reply #82024-09-27
It’s probably caused by interference; check the cable grounding on the control cabinet side
Reply #92024-09-29
If you want to buy a watch, turn to us: Qingdao Automation Instrument Co., Ltd., 15715320097
Reply #102024-11-04
Our company has encountered situations where the flow meter freezes when it exceeds its range; in such cases, it is necessary to turn off the power and restart the flow meter for it to return to normal operation. However, this problem occurs again whenever the range is exceeded. This information is provided for reference only in helping to diagnose the issue

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.