Pressure transmitter range

2025-07-01View Original

Thread Content

Hello, experts. The range of the differential pressure transmitter is 0–3 Mpa, and its measurement range is from -20 bar to 20 bar. Is it okay to use this code? Thank you for the reply.
Reply #22025-07-01
You mentioned that the range of the transmitter is 0~3 MPa (i.e., 0~30 bar), but the actual measurement range of the selected transmitter is -20 bar~20 bar, which is approximately -2 MPa~2 MPa. This indicates that the pressure range you actually want to measure has exceeded the transmitter’s maximum measurement range. Therefore, this code (-20bar~20bar) cannot meet your requirement of a range of 0~3MPa (30bar); you should choose a transmitter model with a range of at least 0~3MPa (for example, 0~30bar or even a wider range). .
Reply #32025-07-02
Thank you for your reply, expert. Feel free to reply again; thanks
Reply #42025-07-02
This post was last edited by xxkhc on 2025-7-5 11:43. It’s not allowed. Because the upper range limit of the differential pressure transmitter is 30 bar, which exceeds the transmitter’s maximum measurement value of 20 bar. This can lead to inaccurate measurements and a risk of damage.
Reply #52025-07-03
But 3 Mpa exceeds the upper limit of the measurement range, so that’s not possible either.
Reply #62025-07-03
-I’ve never seen a transmitter with a pressure rating of 20BAR
Reply #72025-10-16
-Don’t choose 20BAR; it’s not available at the moment.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.