HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Opening direction of substation building doors

2020-09-15View Original

Thread Content

There is a saying that the door located in the middle of the substation building – the door between the high-voltage area and the low-voltage area – should open in the direction of the low-voltage area. I’m not sure which standard or specification this comes from It is only known that GB 50053-2013, the \"Design Code for Substations of 20 kV and Below\", specifies that exterior doors should open outward, while interior doors need to be \"bi-directional spring doors\". There is currently a middle door that opens in only one direction; if it can be ensured to open toward the low-pressure side, the correction will be simpler: lol
Reply #22020-09-15
This post was last edited by myface on 2020-9-15 at 16:10. Beijing Local Standard DB11/527—2015 4.3.2: Doors between equipment rooms and auxiliary rooms shall open in the direction of the auxiliary rooms. The door between the high-pressure chamber and the low-pressure chamber shall open in the direction of the low-pressure chamber. The middle door of the switchgear room should be a two-way opening door. A similar description can be found in item (23) of 3.2.1 in the Handbook for Industrial and Civil Power Distribution Design (4th edition).
Reply #32020-09-16
This post was last edited by btlhrdb2008 on 2020-9-16 09:18. GB 51348-2019 Standard for Electrical Design of Civil Buildings, 4.10.9: The doors of transformer rooms, distribution equipment rooms, and capacitor rooms shall open outward and shall be equipped with locks. When a fire-resistant partition wall is installed between adjacent switchgear rooms, the door in such a partition wall shall be a Class A fire-resistant door that opens towards the low-voltage switchgear room. When the partition wall is installed solely for administrative purposes, the door in it shall be a spring-loaded door made of non-combustible material and capable of opening in both directions.
Reply #42020-09-16
Thank you to the two kind friends upstairs for their help. Sometimes I remember that there are some guidelines, but due to a lack of professionalism and familiarity with them, it’s difficult to find them; professionals know about them as soon as the topic comes up! Thank you:handshake

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.