In the layout of above-ground storage tanks for flammable liquids: 1. Within the same tank group, when the volume of a single tank is less than or equal to ( ), tanks with different fire hazard categories can also be placed in the same group. 2. The total volume of the fixed-roof tank bank shall not exceed ( ). 3. The total volume of floating roof and internal floating roof tank assemblies shall not exceed ( ). 4. The total volume of a tank assembly consisting of fixed-roof tanks and floating-roof or internal floating-roof tanks shall not exceed ( ), where the volume of the floating-roof and internal floating-roof tanks can be calculated as ( ). 1、1000m3 2、120000m3 3、600000m3 4、120000m3 halved (1/2)
http://www.doc88.com/p-77387038372.html Complete Book of Fire Protection Design Codes for Petrochemical Enterprises – available for online viewing O(∩_∩)O Haha~
In the layout of above-ground storage tanks for flammable liquids: 1. Within the same tank group, when the volume of a single tank is less than or equal to 1000 m3, tanks with different fire hazard categories can also be placed in the same group. 2. The total volume of a fixed-roof tank farm should not exceed (120,000 m3). 3. The total volume of floating roof and internal floating roof tank assemblies shall not exceed (600,000 m3). 4. The total volume of a tank farm consisting of fixed-roof tanks and floating-roof or internal floating-roof tanks shall not exceed (120,000 m3); the volume of the floating-roof and internal floating-roof tanks may be calculated as half of that value.
1、1000m3; 2、120000m3 ; 3、600000m3 ; 4. 120,000 m3, halved
1、1000m3; 2、120000m3 ; 3、600000m3 ; 4. 120,000 m3, halved