Issues with the operating power of rotary vane blowers

2018-01-28View Original

Thread Content

The company’s Roots blower has a power rating of 78 kW, a set frequency of 24 Hz, and an operating current of 130 A. Operating power calculated based on current: 1.732*380*130*0.9*0.85=65kw ; Operating power calculated by frequency: 78*(24/50)^3=8.6kw. Experts, could you give some advice? Is there something wrong with my algorithm? Is there a problem with the inverter?
Reply #22018-01-29
The first formula seems plausible, but I don’t understand why the cube of the same frequency is proportional to it in the second formula The rotation speed changes, which affects the flow rate, but not the exhaust pressure (which is determined by the system pressure).
Reply #32023-06-07
Is the operating current the current of the inverter, or the incoming current of the motor?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.