HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

The feedback current from the inverter on the DCS does not match the value at the field

2015-06-05View Original

Thread Content

As the title suggests, a new configuration for the inverter feedback current has been set up in the DCS, but the value displayed does not match the value measured on site. What could be the reasons for this?
Reply #22015-06-05
This post was last edited by budaoweng123 on 2015-6-5 at 10:44. 1. After digital-to-analog conversion by the inverter and analog-to-digital conversion by the DCS, there is definitely some conversion error. 2. Have you added an isolator in the circuit? The frequency converter generates severe electromagnetic interference, and the unequal potential on both sides can lead to errors. 3. Minor error: the measurement ranges on both sides are inconsistent.
Reply #32015-06-05
Is there a problem with the range setting of the DCS? Is the output range of the frequency converter consistent with that of the DCS? You can use a multimeter to measure the current output by the frequency converter and check whether it is correct; then use a loop calibrator to send a 4–20mA signal for testing: lol
Reply #42015-06-05
To ensure better compatibility, the output of inverters may use different signal specifications for various output connections (4-20mA, 0-20mA, 1-5V, etc.). Check whether there are any issues with the wiring, verify that the measurement ranges on both sides are identical, and if that doesn’t work, try using isolators on both sides.
Reply #52015-06-05
For this, what brand of inverter? Schneider?
Reply #62015-06-05
If there is conversion error, can using an isolator solve it?
Reply #72015-06-06
The most common issue with this type of problem is inconsistent range settings. . . .
Reply #82015-06-11
Inverters generally output 1-5V signals; check to see if there is a corresponding value
Reply #92015-06-17
For the current feedback of the inverter, there are parameter settings to adjust the output gain, right?
Reply #102015-06-18
It’s very likely that there’s an issue with the range setting; also, it depends on whether your conversion program is called directly or written by you yourself~!

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.