2015-06-24View Original

Thread Content

When working on-site, 24V+ ground connection does not cause the fuse to blow, but when working on a certain device before, I encountered a situation where 24V+ ground connection led to the fuse blowing. May I ask: Under what circumstances will it burn out? Under what circumstances will it not burn out? Thank you.
Reply #22015-06-24
It’s all in short circuit; why can’t the fuse blow?
Reply #32015-06-24
It’s all in short circuit; why can’t the fuse blow?
Reply #42015-06-24
There are also those that won’t burn out. Under what circumstances won’t they burn out?
Reply #52015-06-24
For systems with floating power supply (where the power system has no ground), 24V+ground will not blow the fuse.  
Reply #62015-06-25
The statement on the 5th floor is correct; if terminal 24 is grounded and then terminal 24+ is also grounded, the fuse will definitely blow!
Reply #72015-06-25
Without a closed circuit, there is no current; without current, the fuse will not blow, unless there is a high-voltage breakdown. 24+ ground means that this potential is set equal to the ground potential, at which point the reference point of the power supply is -24V.
Reply #82015-06-25
Agree with the view on floor 5; it burns out when the negative terminal is grounded.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.