I would like to ask fellow sailors: the pressure at the inlet of the steam trap is 9 kilograms, while the pressure at the outlet is 4 kilograms, as calculated based on the pressure difference in the system downstream of the valve and the pipeline resistance. So what causes the 5-kilogram pressure difference across the steam trap? Is it due to the internal structure of the valve or some other factor? Please advise
Reply #22015-09-14
A leaking check valve, a leaking bypass, and rising pipeline elevation can all lead to an increase in back pressure.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.