Steam flash tank, with steam condensate as the medium; operating pressure of 1.6 MPa, operating temperature of 201°C, and operating density of 865 kg/m3. It is equipped with an electric float level gauge and a magnetic flap level gauge. It has been in use for over 5 years, and recently there has been a discrepancy between the two gauges – when the liquid level is below 30%, their readings are fairly similar. However, as the liquid level rises, the discrepancy increases, reaching up to 35% in some cases. Help needed! ! ! ! ! !
Check whether there has been a change in the medium density, and whether the weight of the float has changed...
? ? ? ? ? ? ? ? ????????????
:'(:'(:'(:'(:'(:'(:'(:'(:'(:'(
Although there are some minor changes, the problems are not serious
Please, experts! Solve! :'(:'(:'(:'(:'(:'(:'(:'(:'(
The best and most thorough way to solve the problem is to calibrate the float level gauge on-site.
It was repaired, but the problem appeared again after a short time – should the torque tube be replaced?
Check the magnetic flip switch as well; there could be a problem there as well, it’s not necessarily an issue with the electric float.
For these reasons, the possibility of a problem with the circuit board cannot be ruled out; issues such as aging of electrical components and reduced performance may occur, and these can be addressed by replacing the components one by one.
The magnetic flap has been checked – no problems!