The probe is intrinsically safe, the cable is also intrinsically safe; since the transmitter is located outside the explosion-proof area, is it still necessary to have an intrinsically safe design?

2015-10-29View Original

Thread Content

It’s a split-type instrument; the probe is intrinsically safe, as is the cable. I install the transmitter outside the explosion-proof area – does that mean the transmitter also needs to be of the intrinsically safe explosion-proof type?
Reply #22015-10-29
The transmitter does not need to be intrinsically safe, but a safety barrier must be added between the transmitter and the field; only then is it an intrinsically safe circuit.
Reply #32015-10-30
Thank you, moderator. I have used safety barriers between field transmitters and DCS systems, but I have not used ones between transmitters and the sensors in the field. What type of safety barrier is generally suitable for such cases? PS: This meter is a common E+H split-type pH temperature meter; the electrodes collect pH and temperature signals and send them to the field transmitter. The cable connecting the electrodes to the transmitter is provided by the manufacturer and is a four-wire cable.
Reply #42015-10-31
1. The PH probe has a intrinsically safe circuit; the safety barrier is located inside the transmitter, forming the intrinsically safe \"probe detection circuit\". You can take a look at the circuit diagram. 2. As for the explosion-proof measures used by the transmitter itself, it depends on the area where it is installed; there are Exd or E* options available ; If it is in a safe area, the transmitter body does not require explosion-proof certification. 3. The intrinsically safe approach for 1 is referred to as “associated,” and this is indicated with parentheses; check whether there are parentheses on the explosion-proof marking of the transmitter 4. Similar to PH, the signals from capacitive level sensors, electromagnetic flowmeters, and mass flowmeters are all processed by safety barriers built into the transmitters; since the detection circuits can be designed to be intrinsically safe, there is no need for explosion-proof designs – something that would be unnecessary and overly complicated. . . . @jiaguoyun
Reply #52015-11-03
Every component in the circuit must be intrinsically safe; non-explosion-proof components can be used once one exits the explosive hazard area (for electrical systems isolated from the outside world in the control room)
Reply #62016-01-08
Intrinsic safety is actually quite complicated: not only must the individual components be intrinsically safe, but an intrinsic safety cable, an intrinsic safety power supply, a safety barrier, and other elements are also required to form an intrinsic safety circuit. As the person above said, \"Every component in the circuit must be intrinsically safe.\"”

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.