Under what circumstances is a settler required for a differential pressure flow meter?
Reply #22015-11-08
When measuring gas and the differential pressure transmitter is below the measurement location
Reply #32015-11-08
1 The gas contains large particles of dust and impurities. 2 Install at a low position
Reply #42015-11-08
When the medium has high viscosity, is corrosive, or has a freezing point higher than the ambient temperature, measures such as isolation, heating, or purging should be taken; In the presence of solid particles or dust, purging or isolation measures are advisable.
Reply #52015-11-08
When measuring gas and the differential pressure transmitter is below the measurement location
Reply #62015-11-08
When measuring the flow rate of liquids containing impurities or humid gases, a sediment trap and a drain valve should be installed at the lowest point of the conduit, in order to collect and regularly remove various contaminants and accumulated water from the signal pipeline.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.