Why can the EJA110A differential pressure transmitter output only one type of differential pressure?

2015-12-19View Original

Thread Content

An 110A differential pressure transmitter used in conjunction with a standard orifice plate to measure flow, with a range of 0–6 KPa; its output current is only 5.4 mA. A differential pressure of 0.308 KPa corresponds to a flow rate of approximately 1400, while the full scale flow rate is 5000. First, I checked the installation direction of the orifice plate and the pressure tapping pipes, and found that the direction was correct with no leaks. After replacing it with a different differential pressure transmitter and connecting the handheld controller, the differential pressure value was 1.7 KPa, which is close to the actual flow rate. Why could the first transmitter only output one differential pressure value? What are the solutions? Can the original transmitter still be used?
Reply #22015-12-19
It is likely that the differential pressure setting of the differential pressure transmitter does not match that of the orifice plate; otherwise, there may be a problem with the differential pressure transmitter.
Reply #32015-12-19
Do you have it set to output current or voltage? It seems that the differential voltage value you have doesn’t correspond to the output signal.
Reply #42015-12-19
Current output – the figures I mentioned might not be entirely accurate, but after switching to another unit, the readings seem correct
Reply #52015-12-20
The original poster hasn’t mentioned many issues, so it’s impossible to analyze! Just replace it with a new one casually? ? Okay! ! First, an orifice plate is usually equipped with a three-valve assembly; close the primary valve and open the balance valve to see if the reading returns to zero ? I don’t understand what you mean by saying that only one differential pressure value can be output – I’m confused by that statement! ! ……Wait for questions, wait for judgments – in my opinion, the original poster, this isn’t something that constitutes a problem at all! You can learn more on the forum!
Reply #62015-12-20
If the transmitter’s output signal does not change with the measured signal, it may be because the transmitter is in loop calibration mode and has not been exited.
Reply #72015-12-20
What to do if a one-way valve has internal leakage? It is recommended to close the positive and negative pressure valves of the one-way valve directly, remove the pressure tapping tube connected to the transmitter, and check whether the reading returns to zero. GG
Reply #82015-12-23
It seems to be the difference between square-root output and non-square-root output.
Reply #92015-12-23
If everything is normal, I agree with the view above: some involve taking the square root of instruments, while others involve taking the square root of DCS values – this must be kept in mind. A differential pressure value,,, um,,,
Reply #102015-12-27
It should be a square root problem, as mentioned above, plus there are issues related to the actual site conditions; the original poster also didn’t clarify what was being measured. Here, one of the steam flow meters has been installed improperly. It was correct before the isolation tank was installed, but afterward the pressure tapping pipe bent upward, causing the meter gauge to be above the isolation tank. The insulation was inadequate, and after it was put into use, condensation occurred rapidly on the high-pressure pressure tapping pipe on the north side, resulting in false readings that were lower than the actual flow rate

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.