Can a storage tank equipped with a breather valve be fitted with a single-flange level gauge?

2016-01-04View Original

Thread Content

Several storage tanks in our plant are equipped with breather valves, but they are designed with single-flange level gauges; I wonder if these work well
Reply #22016-01-04
Yes, that’s the case with multiple atmospheric pressure storage tanks.
Reply #32016-01-04
Does the breather valve open only when a certain pressure is reached? The single-flange level gauge installed in my home is connected to the atmosphere under negative pressure; does the liquid level also rise during the process of pressure increase?
Reply #42016-01-04
If it is a sealed storage tank, it is recommended that you use a dual-flange differential pressure gauge for measurement
Reply #52016-01-05
This post was last edited by HEJIYUER on 2016-1-5 at 00:49. Based on this analysis, assuming the pressure in the tank is less than 2 KPA, using a double-flange LT with a measurement range of 5 meters results in a pressure of approximately 50 KPA, which corresponds to 100% liquid level. So for a single-flange PT gauge showing 52 KPAG, which corresponds to 100% liquid level, the error is only that much. But when the liquid level drops, this error becomes larger. If a low-level alarm is required, it is best to connect the negative pressure chamber as well, making it an LT ; If there is only a high alarm, the original poster’s approach is acceptable. @jiaguoyun
Reply #62016-01-05
Agreed! Atmospheric pressure is not the same as normal pressure
Reply #72016-01-05
When using a differential pressure transmitter to measure liquid level, its range is usually only in the range of a few dozen KPa; the pressure at the top of the container has a significant impact. Moreover, devices such as safety valves and nitrogen seals can sometimes be unstable as well. Therefore, unless it is an open-container setup, the low-pressure side of the differential pressure transmitter must be connected to the top of the container.
Reply #82016-01-05
When using a differential pressure transmitter to measure liquid level, its range is usually only in the range of a few dozen KPa; the pressure at the top of the container has a significant impact. Moreover, devices such as vent valves and nitrogen seals can sometimes be unstable as well. Therefore, unless it is an open-container setup, the low-pressure side of the differential pressure transmitter must be connected to the top of the container.
Reply #92021-01-03
I haven’t been here in a long time. . . . .

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.