What is the current of a 55kw, grade 8 motor? How to calculate
Reply #22016-01-06
This post was last edited by chb1534 on 2016-1-6 at 15:07. Theoretically, P=1.732UI*0.85 (power factor); in practice, the motor efficiency also needs to be taken into account. For a 55KW motor, the efficiency is generally around 0.90-0.95, so 0.9 will be used for calculation purposes here. P=1.732UI*0.85*0.9; therefore, for a 55KW motor, the current I=55000/1.732*0.85*0.9*380=109.2A. The efficiency and power factor can be set at lower values here; if the motor is of better quality, the current will be less than 109A, but generally it will not be less than 100A. Additionally, level 8 is only related to speed and has nothing to do with current.
Reply #32016-01-07
Reference can be made to Chapter 9 of the \"Manual for Industrial and Civil Power Distribution Design (3rd Edition)\"
Reply #42016-01-10
Estimate for a 3-phase asynchronous motor at 380V, using 2A per kilowatt
Reply #52016-01-16
The current is 105A, with a fluctuation of 2A up or down.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.