Can pipe trenches be built inside a fire dike?

2016-07-28View Original

Thread Content

In the methanol tank area, it is necessary to collect the methanol from the drain lines and discharge streams into a main pipe, which will then be connected to the underground methanol tanks; Since the main pipe slopes toward the underground tank, it is possible to dig a trench within the fire dike, place the main pipe there, and fill it with sand.
Reply #22016-07-28
There should be no problem with this, provided that it is ensured that the oil that leaks inside the tank area does not seep outside the fire dike through the trench.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.