Piping issues in centrifugal refrigeration units

2016-01-20View Original

Thread Content

Trane portable chiller units, with a cooling capacity of 4500 kw per unit. 1. Should flexible connections be installed at the water inlet and outlet ports of the evaporator and condenser? Is it necessary to set it, or are there any principles? 2. How should the pressure gauges and temperature gauges on the inlet and outlet pipes be installed? Must pressure gauges be installed on the inlet and outlet water pipes?
Reply #22016-01-25
The factory manual provides recommendations regarding the piping procedures. Since it’s a centrifugal compressor, there isn’t much vibration, so there’s no need to use flexible connectors; any unnecessary instrumentation should be avoided (does the pressure gauge need to be calibrated?) ), filters, as well as the venting at the top and the bottom drain valve are still very necessary

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.