Flow meter issues related to signal transmission

2016-03-08View Original

Thread Content

The flow measurement using steam orifice plates in the company experiences large fluctuations. Upon on-site inspection, the gauge (Rossmount 3051 model) showed normal readings, and the current output was also normal; however, for some reason there were significant fluctuations in the control room. Could it be that the signal wires are not properly grounded?
Reply #22016-03-08
Check whether the channel is functioning properly; it is recommended to use a return current tester to test the current channel. Also check the instrument wiring to see if there is interference from high-voltage equipment.
Reply #32016-03-08
The central control signal was checked using a multimeter tester, and the readings were normal with no fluctuations in the data
Reply #42016-03-08
Is there no reflux checker? Or a process verifier would work too... What you measure with a multimeter isn’t necessarily accurate; based on what you’ve described, there seems to be some interference... Is the shielding network grounded?
Reply #52016-03-08
I just performed a signal detection; I turned the power off and reset it, and now it’s showing normal again.
Reply #62016-03-08
Maybe it’s due to poor contact; clean it with a vacuum regularly……
Reply #72016-03-08
Take a look at the shield grounding; there is interference.
Reply #82016-03-08
Grounding the shield at two points can cause common-mode interference; this occurs when shielding is already grounded in the control room and grounding is provided elsewhere at the site
Reply #92016-03-08
Oh, I see. I’ll check the shielding and grounding carefully then. Thank you

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.