I have a question~ What are the requirements for installing an outdoor vacuum circuit breaker indoors?

2016-07-12View Original

Thread Content

I currently have a ZW32-12 outdoor vacuum circuit breaker, and I would like to install it indoors. What are the requirements for such installation? For example, are there any regulations regarding the distances in the up, down, left, and right directions? It’s not in line with the standards by half a step; I don’t understand how to do it, so I’ve come to ask for advice
Reply #22016-07-17
This is mainly to ensure the safety of people coming in and going out; the safe distance for 10kV voltage is 0.7 meters, so you should also leave a one-meter gap around it. The room needs to be protected from small animals, and also the area should be on a high elevation to prevent flooding

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.