Installation location of the human body static electricity discharge device

2016-04-08View Original

Thread Content

As the title suggests, should an anti-static discharge device for the human body be installed outside or inside the protective dike of a tank farm? Which standard should be followed?
Reply #22016-04-08
It’s outside; one must eliminate static electricity before entering the tank area.
Reply #32016-04-08
One is installed at each entrance to the tank area outside the protective dike, and another one is installed next to the ladder of each tank.
Reply #42016-04-12
It must be installed outside; static electricity must be eliminated outside before entering the explosion-proof area
Reply #52016-04-12
HG20451 4.2.10 shall be installed at the entrance to flammable and explosive areas.
Reply #62016-04-13
Ours is installed at the entrance to the tank area, outside the protective fence

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.