Mass flow meter issue, waiting online

2016-04-13View Original

Thread Content

A mass flow meter, from Emerson’s 1700 series. The on-site meter display is normal, and the output current signal is also normal. However, after the signal is connected to the PLC (Mitsubishi PLC analog card), the pump operates normally during the first 20 seconds, but thereafter no display is shown on the screen, although the current signal remains normal. Need help. Waiting online; it’s really frustrating
Reply #22016-04-13
When you say the output current signal is normal, do you mean the value measured when the output current signal circuit is disconnected, or the value measured by a milliampere clamp meter?
Reply #32016-04-13
What is the voltage measured on the PLC side when the output current signal circuit is disconnected?
Reply #42016-04-13
0V confirms that the PLC is passive
Reply #52016-04-13
So, what is the voltage on the mass flow meter side when the output current signal circuit is disconnected?
Reply #62016-04-13
So, what is the voltage on the mass flow meter side when the output current signal circuit is disconnected?
Reply #72016-04-13
So, what is the voltage on the mass flow meter side when the output current signal circuit is disconnected?
Reply #82016-04-13
All signals that can be monitored on-site at 24V and via the PLC have been checked; everything is normal
Reply #92016-04-13
Oh, that only indicates whether there is a problem with that channel in the PLC. Disconnect that channel from the PLC completely and supply it with a passive signal of 4–20 mA to see if anything appears on the display
Reply #102016-04-13
The PLC channel was also changed, but it didn’t work; when another flow meter was connected to that channel, everything worked fine! My head is killing me; I’ve been working on it for 2 days

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.