We have a mass flow meter from Shanghai Yino; a power supply module is installed on-site to provide 24V power for the instrument to function properly. With the same power supply, the instrument connected directly from the DCS does not work. Please help solve this issue
Reply #22016-05-14
The mass flow meter has separate power and signal wires; it is a four-wire instrument, so please confirm whether that is the case. If the cable is four-wired, verify the resistance of the power return circuit again; the voltage is insufficient.
Reply #32016-05-15
It is likely that the cable is too long, resulting in a large voltage drop and thus the load voltage failing to meet the minimum requirement specified by the instrument
Reply #42016-06-19
This post was last edited by massflowmeter on 2016-6-21 09:25. Sorry, I deleted it myself.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.