It is a double-flange level gauge with capillaries, the flange spacing being 1000 mm (the medium is water). After installation, the transmitter signal is sent to the DCS; is it necessary to perform zero-point adjustment on the transmitter?
Reply #22016-05-20
Both double-flange level gauges and level transmitters require zero-point negative migration.
Reply #32016-05-20
Differential pressure level measurement generally requires calibration; otherwise, the level reading will be inaccurate
Reply #42016-05-20
Migration is required; after installation, simply make the adjustment at the lowest liquid level.
Reply #52016-05-20
Migration must be carried out; the differential pressure displayed after installation but before operation serves as the amount of migration
Reply #62016-05-23
Is “resetting to zero” also called zero-point migration now?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.