The issue of instrument signal interference

2016-05-27View Original

Thread Content

I’d like some advice. Currently, the temperature signal of the chiller is experiencing fluctuations; it is preliminarily assumed that this is caused by interference. I’m not sure what methods can be used to resolve this issue. Thank you!
Reply #22016-05-27
Excluding any issues with the wiring equipment, you can try covering the signal cable with a metal hose
Reply #32016-05-27
After talking for so long, they still didn’t say what the interference was Is there electromagnetic interference in the engine unit now? Does vibration cause uneven temperature measurement in the resistive core? Does the cable not have a shielding layer?
Reply #42016-05-27
The signal wires use shielded wiring and are properly grounded....
Reply #52016-05-27
I have encountered this too; the reason is that the cable supplied by the chiller manufacturer does not separate the high-voltage and low-voltage signals. Re-lay it according to the specifications. Make sure the shield wire is grounded in accordance with the specifications.
Reply #62016-05-27
In our reactor, we also experienced a situation where one temperature measurement increased from 71 to 74; 75 is the critical value. At that time, we didn’t know what the cause was
Reply #72016-05-27
Excluding any issues with the wiring equipment, you can try covering the signal cable with a metal hose
Reply #82016-05-27
The power supply section of the sensor also needs to be isolated
Reply #92016-05-27
Try adding a signal isolator and measure the grounding of the signal line
Reply #102016-05-29
Check the grounding and shielding, as well as the wiring; ensure it is securely fastened, especially in front of the transmitter and the gauge. Inadequate fixation can lead to a semi-loose connection due to external factors such as vibrations. Another factor is the quality of the transmitter; poor quality or aging can cause fluctuations in the measured values. The cable connected to the transmitter should be shielded. If the primary instrument is a buried type, it is recommended to replace it; even if it isn’t buried, it’s still advisable to replace it and observe the performance thereafter. The temperature signal should not experience jumps, but this has happened several times; this topic deserves further discussion.
Reply #112016-05-30
Where does the original poster work? We have four ice makers here as well

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.