The output of the Chuanyi electromagnetic flowmeter remains at 4 milliamps

2016-05-31View Original

Thread Content

The table header displays correctly, but the output in milliamps is always 4 milliamps! The forced analog signal is also 4 milliamps!
Reply #22016-05-31
Check the instructions to see whether an active or passive signal is required, and whether it needs to be superimposed
Reply #32016-05-31
Is it in “circuit verification” mode?
Reply #42016-06-01
If it is in circuit test mode, simply turn off the power. If it’s passive, there should be no current flow; it’s also impossible for the Hart address to be set to a non-zero value
Reply #52016-06-02
Check whether Chuanyi supports the Hart protocol; if not, use BT2000 to connect. It seems that your settings are in circuit verification mode, so the output is forced to 4 mA

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.