Does the ammeter show no reading after the water pump starts?

2016-07-09View Original

Thread Content

I’m an operator; one of our air separation unit’s cooling water pumps doesn’t show any current reading after it’s started, although it used to work fine before. We reported it to the electrician team, and they spent the whole morning checking things – examining the distribution cabinets and the wiring of the control panels. Later, they asked us to try restarting it again, but it still didn’t display anything. In the end, they told us that it was the ammeter that had burned out, saying something about the ammeter not being compatible and about electromagnetic transformers. . . Just a 7.0 or a 7.5 is enough to burn out the ammeter. I’m a complete beginner; could some kind person please explain it to me? Thank you
Reply #22016-07-09
It’s like it got damaged due to exceeding the range, right?
Reply #32016-07-09
Ammeters come in types with and without current transformers. The current transformer is used to convert high currents into 0–5A currents that are then sent to the ammeter for display. If the ammeter gets damaged, it may be due to excessive current; it is necessary to identify the cause of the high current before replacing the ammeter.
Reply #42016-07-10
The ammeter of the pump burns out normally; it can burn out just like a light bulb
Reply #52016-07-12
Thank you, teacher. With your explanation, I finally understand😊

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.