Power supply issues with 3-phase 4-wire incoming distribution cabinets

2016-08-24View Original

Thread Content

The power supply coming from the transformer is three-phase four-wire, and what is distributed through the distribution cabinet is also a three-phase four-wire system. However, the distribution cabinet contains control components such as contactors; so is it better for the control circuit to use a voltage of AC 380V directly, or should a neutral wire be provided inside the cabinet to use a voltage of 220V? Or use a transformer to convert 380V to 220V?
Reply #22016-08-24
It’s fine to use a direct AC 380V voltage, or to separate a neutral wire inside the cabinet to use 220V voltage; there’s no need for a transformer. After all, every additional device represents an extra point of failure, so there’s no need to include a transformer

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.