Wiring of pneumatic cut-off valves and control valves

2016-09-30View Original

Thread Content

Why do pneumatic cut-off valves use a six-wire connection system, while pneumatic control valves use a two-wire system? What do DI/DO, AI/AO correspond to in a DCS?
Reply #22016-09-30
The input signal for the control valve is a 4-20mA current signal, transmitted over 2 wires; Cut-off valves are generally controlled by solenoid valves, which require 2 wires. Cut-off valves usually need 2 position switches to indicate the valve’s operating state, and these position switches require 3 or 4 wires. DI: Digital input ; DO: Digital output ; AI: Analog input ; AO: Analog output.
Reply #32016-09-30
Activate the cut-off valve; there are feedback signals via two or three wires, including two DI points and one DO point. Feel free to ask if you have any questions
Reply #42016-09-30
DO 1: Solenoid valve signal; DI 2: Valve open position, Valve closed position
Reply #52016-10-01
The answer on floor 4 is not as good as that on floor 2 – how can it be chosen as the best?
Reply #62016-10-01
The input signal for the control valve is a 4-20mA current signal, transmitted over 2 wires; Cut-off valves are generally controlled by solenoid valves, which require 2 wires. Cut-off valves usually need 2 position switches to indicate the valve’s operating state, and these position switches require 3 or 4 wires. DI: Digital input ; DO: Digital output ; AI: Analog input ; AO: Analog output. Two DI points, one DO point. For the DO point: one for solenoid valve signal, and two for valve position – open and closed. I’ve learned it.*
Reply #72024-04-03
Can a pneumatic on-off valve with feedback be powered directly by a single 6-core control cable with overall shielding?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.