Safety issues related to the use of negative pressure systems in tank areas to prevent uncontrolled emissions of waste gases

2016-12-21View Original

Thread Content

Acidic substances stored in tanks, such as hydrochloric acid and phosphorous acid, can produce significant gas emissions when exposed to moisture during rainy weather. When negative pressure devices are used to absorb these exhaust gases, a vacuum is created inside the tank, which can cause damage to the tank. What measures can be taken or what devices can be installed to prevent the formation of this vacuum and ensure safe operation?
Reply #22016-12-21
It is not connected to the vent port and kept at a certain distance. It is best to design the vacuum port in a trumpet shape, with the tank’s vent extending slightly into this trumpet shape. It can absorb mist without creating excessive negative pressure inside the tank.
Reply #32016-12-21
It’s not that we are very familiar with your actual situation, but we have a storage tank for concentrated sulfuric acid (98%), along with a drainage pipeline that leads to a ditch. There is a drying device installed on this pipeline, filled with a large amount of desiccant; the desiccant is replaced regularly. Additionally, I wonder if it would be possible to install a gas seal device on your tank to maintain a slight positive pressure, so that air can be introduced into it when the pressure drops. (Example: N2 envelope)
Reply #42016-12-22
A breathing valve can be used. For better performance, a nitrogen seal valve combined with a single exhaust valve can be used.
Reply #52016-12-22
Regarding the items that come after this air respirator, I consulted the Safety Supervision Bureau and received a reply stating that a refrigerated dryer can be added
Reply #62016-12-22
On the top of our storage tank, there is only one negative pressure port and one feed port. Yesterday, employees created negative pressure, which resulted in a vacuum inside the tank and damaged the tank’s roof. Fortunately, the tank was empty, so the tank body was not damaged
Reply #72016-12-22
Is it possible to install a pressure detection device that automatically stops the vacuuming equipment when the pressure reaches a certain level?
Reply #82016-12-22
1. A liquid seal is used, with an alkaline substance as the liquid in this seal to absorb acid mist. A vent valve is installed on the liquid seal tube; it should be closed when feeding material into the tank, and opened when discharging material, in order to prevent a vacuum from forming inside the tank. 2. If the diameter of the negative pressure port mentioned by the poster is large, two pipes can be welded to the flange of that port: one connected to the fan and the other used for evacuation.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.