There is a safety valve pipeline; the set pressure of this safety valve is 1.6 MPa. The outlet of the safety valve leads to another vent main, to which gas venting pipelines are connected, and the discharge pressure for these gases is 1.5 MPa. During design, can the outlet pipeline of the safety valve be connected to this main?
Reply #22017-08-14
The back pressure is determined by the flare network, typically ranging from 0.5 to 2.0 bar.
Reply #32017-08-14
Whether the pressure at the key connection point meets the backpressure requirements specified in the safety valve calculation sheet
Reply #42017-08-15
The design manual states that if the safety valve vents directly to the atmosphere, it requires its own pipe, and it cannot be connected to a common pipe
Reply #52017-08-15
The design manual states that if the safety valve vents directly to the atmosphere, it requires its own pipe, and it cannot be connected to a common pipe
Reply #62017-08-16
Could you elaborate? Is it sufficient that the inlet pressure is not greater than the back pressure specified in the safety calculation sheet?
Reply #72017-08-16
If the pressure at the inlet is higher than the backpressure specified in the calculations, then the discharge capacity of the safety valve will not be sufficient. Additionally, it is necessary to consider whether the pipe diameter is adequate for discharging both materials together.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.