The distance between the cabinet and the wall

2022-03-02View Original

Thread Content

"Control Room Design Specifications" 3.3.10 The area of ​​the cabinet room should be determined based on the size and quantity of the cabinets and comply with the following regulations: 2 The clear distance between the cabinet and the wall (column) should be 1.6~2.5 meters. Nowadays, some fine chemical companies only use single-sided cabinets. What should be the distance between the single-sided cabinets and the wall?
Reply #22022-03-06
Why use a single-sided cabinet? Are there so few points?
Reply #32022-03-07
Yes, Fine Chemicals only has one reactor
Reply #42023-03-27
I have also recently consulted on related issues, and the explanation given by the designer: The explanation given in the HG/T20508 control room design specification is that 1.6~2.5m is the distance used as a pedestrian passage. If it is not a pedestrian passage, it can be leaned against the wall (preferably ≥500mm). This was the understanding of experts during the standard discussion at the time, but it was not written out in the standard. For electrical majors, the distance between distribution cabinets and walls or pillars stipulated in the substation design specifications is very clear.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.