Should gate valves or globe valves be used at the inlet and outlet of the high-pressure feed water pump? In our company’s medium-temperature and medium-pressure boilers, the atmospheric deaerators, and feed water pumps have gate valves at the inlet and globe valves at the outlet. The valve core of the inlet gate valve has fallen off twice; some people suggest using globe valves instead, but those who are against this idea say that gate valves were used in the original installation and therefore cannot be changed. Dear experts, what kind of valve should be used? What is the basis?
Since the inlet pressure of the pump is relatively low, gate valves are usually chosen; valve selection is very important: lol
The inlet and outlet valves of our boiler feed water pumps are all gate valves, and we have never seen the valve cores fall out. Imports are usually left open and not closed, so gate valves are a good choice.
It was the right choice to use a gate valve at the water inlet; indeed, it is not recommended to replace it with a globe valve – instead, one can try using a gate valve with a higher pressure rating.
Gate valves are generally used for pump inlets and outlets as they offer low resistance!
It is recommended to use butterfly valves; those with a pressure rating of 1.6 MPa will perform well. These cast iron gate valves are products from small workshops and are cheap. As required, it comes with a worm gear transmission mechanism and a handle; the valve port can be either soft or hard. It is recommended to choose a handle-type model; for the valve port, decide based on the temperature requirements. Purchase from Taobao Duoduo. (For reference)
Gate valves or butterfly valves can also be replaced with other types of valves, depending on the specific operating conditions and your project budget. Dual gate valve configuration is preferred.
There is a reason for choosing gate valves at the entrance: they feature rapid operation and high flow rates. If the valve head comes off, is it a problem with the quality of the valve? An update can be considered.
Generally, it is a combination of a gate valve and a check valve.
We carry out project installation on-site; generally, gate valves are used for the inlet and outlet of pumps