Question: To cool 8 tons of steam at 105 degrees Celsius and a pressure of 30 KPa to a liquid state, how much circulating water is required? The temperature of the circulating water is 32 degrees Celsius.
Reply #22018-04-10
Find the latent heat corresponding to the steam; determine how much cooling water is required for heat balance calculations using this latent heat
Reply #32018-04-10
If a condenser is used, calculations are needed, as well as for the fouling thermal resistance. It’s not about theoretically considering heat balance.
Reply #42018-04-10
The latent heat of vaporization of low-pressure steam is approximately 2200 kJ/kg. With a temperature rise of 10°C for the circulating water, about 420 tons per hour of circulating water is required.
Reply #52018-04-10
It is relatively easy to calculate using both the enthalpy and entropy of steam; in addition, the temperature rise of the condensed water is also required. It’s actually a simple heat exchange calculation. However, the enthalpy value of steam and that of water at 100° need to be looked up; it’s just a bit tedious.
Reply #62018-04-11
This post was last edited by arpcd on 2018-4-11 at 13:48. Questions related to factory auxiliary engineering that experienced engineers and veterans can easily answer. The amount of water required for circulation to condense one ton of low-pressure steam can be estimated fairly easily. In the southern region (the designed temperature difference for circulating water is 5°C, ranging from 32°C to 37°C), with a ratio of 100 tons of circulating water per ton of steam, the water flow rate would be 8 x 100 = 800 tons per hour. In the north (the designed temperature difference for circulating water is 10°C, with a range from 32°C to 42°C), based on a ratio of 50 tons of circulating water per ton of steam, the capacity is 400 tons per hour. . For the latent heat of vaporization of low-pressure steam, you can use 500 kcal/kg as an estimate; it’s not entirely accurate, but the precision for estimation is sufficient. . .
Reply #72018-06-03
This post was last edited by Catalyzing a Grain on 2018-6-3 at 16:47. The recycled water returns at 40 degrees, amounting to roughly 575 tons.

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.