The 3051s Sam electronic remote differential pressure transmitter cannot detect the low-pressure side

2017-10-21View Original

Thread Content

This post was last edited by chen1711 on 2017-10-21 at 21:52. The diaphragm on the high-pressure side is damaged; after replacing it separately, the low-pressure side cannot be found. Why is that? Does anyone know the answer?
Reply #22017-10-21
This post was last edited by tiger2010 on 2017-10-21 22:02. Have the HART menu PHI and PLO module assignments been done?
Reply #32017-10-21
SET PHI-PLO or SET PIO-PHI?
Reply #42017-10-21
It’s set up for measurement, but the low-pressure transducer cannot be found. It has become a single-flange measurement, I guess. By switching back to the original setting, the pressure on the PLO side can be seen
Reply #52017-10-21
It’s set, but I still can’t find the low-voltage side. The concern is that it’s a single-flange measurement, so they dare not use it
Reply #62017-10-21
:Can it be measured? With PHI and PLO set, can the main transmitter output the current value calculated from the differential pressure?
Reply #72017-10-21
There is an output, but it is not exactly the differential pressure value; 475 indicates that the low-pressure side module cannot be found
Reply #82017-10-21
Is there a detailed settings menu?
Reply #92017-10-21
Yes, the official website also has instructions for this ERS table. Do you need the instructions or the menu?
Reply #102017-10-21
It would be good to have a menu. The official instructions are quite simple; they aren’t detailed user guides

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.