Based on past design experience, communication signals should not be used only for alarm and display purposes; they cannot be utilized for control and interlocking functions. But no relevant regulatory provisions can be found; I seek advice from experts – which standard contains relevant descriptions.
Reply #22017-11-10
As I recall, some guidelines state that it is not allowed or not recommended to use communication signals in chaining
Reply #32017-11-10
It cannot participate in interlocking regardless of whether there are regulations or not. The communication is unstable and prone to interference; if involved in interlocking systems, be prepared for a lot of hassle, as it will be difficult to identify the source of the faults.
Reply #42017-11-11
Communication signals can only be used for alarm and display purposes; they cannot be used for control or interlocking. What communication signal? Is the Internet considered a communication signal these days, and is it stable?
Reply #52017-11-13
For instruments, signals transmitted over network cables are considered communication signals, as opposed to those transmitted via direct wiring.
Reply #62017-11-13
No standards are needed; the delay of communication signals is generally at least 3 seconds or more. How can such a delay be used for control sequences? This single fact is sufficient. The 3-second device might have exploded already
Reply #72017-11-13
One can refer to GB/T50770 \"Code for Design of Safety Instrumented Systems in Petrochemical Industries\" and HG/T 20511-2014 \"Code for Design of Signal Alarm and Interlock Systems\", which specify the requirements regarding the use of communication signals in interlock systems. Communication signals cannot be used in interlocking.
Reply #82017-11-14
Both of these specifications do mention something related to chains, but they don’t state that communication prevents participation in or control over chains
Reply #92017-11-14
The issue lies with Siemens’ safety modules; the SIS interlock signals are all transmitted via communication, using DP PN and other protocols. As long as there is authentication for such communication, I think it should be fine.
Reply #102017-11-14
Clause 6.1.5 of GB/T50770: Measurement instruments shall not use fieldbuses or other communication methods as input signals for safety instrumented systems.
Reply #112017-11-20
Are all bus-type instruments that transmit signals via communication unable to participate in interlocking? ? I don’t know what you mean. Maybe what you mean are the security level requirements? ? ?

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.