HCBBS Forum (English)
Submit Chemical Projects / Find Solutions
Amplify Your Requirements on a Broader Chemical Platform *Engineering · Technology · Equipment · Solutions*
Submit Request

Two questions about the MLD-PVI block of CS3000

2018-01-09View Original

Thread Content

I’ve been encountering some issues while looking at the MLD-PVI block of the CS3000 recently. I’m not very familiar with the CS3000, so my questions might be a bit basic; please don’t be harsh on me. As shown in Figure 1 below, what do the terms “Data Reference” and “Data Setting” mean in the table regarding the connection methods of the input and output terminals? What is the difference? Also, under what circumstances is the “tracking mode” in Figure 2 used? If, in a control module, there is a PID block at the higher level, with an MLD block connected in series, and the output of the MLD block is connected to the I/O, I would like to ask: how can a smooth transition be ensured when the MLD block switches from MAN/AUT mode to CAS mode, or vice versa? Are there any settings that need to be made in the MLD or PID block? Thank you~!
Reply #22018-01-09
Pictures can’t be uploaded, so post the message first and add the pictures later~
Reply #32018-01-10
The last edit to this post was made by jlshnlhj on 2018-1-10 at 16:03. Connecting the data from an upstream “module” to the input terminal of a downstream “module” is called data reference. Connecting the output terminal of an upstream “module” to the data of a downstream “module” is called data setting. Connecting the output terminal of an upstream \"module\" to the input terminal of a downstream \"module\" is called terminal connection. What you call MLD should actually be MLD-SW; either AUT or CAS can be chosen, and in all cases these values are provided externally. Does the output experience disturbances when MLD-SW is set to manual and changed to AUT or CAS?
Reply #42018-01-11
Hello there upstairs, thank you very much for your reply. I would like to ask: within a module, how are \"data\" and \"terminals\" distinguished from each other? Which ones are considered data and which ones are terminals? Thank you~
Reply #52018-01-11
Why still can’t I upload pictures these days!
Reply #62018-01-11
This post was last edited by jlshnlhj on 2019-8-20 09:12. The various modules are different, but all come with detailed explanations. For example, in a cascade PID module, the output of the preceding stage (refer to OUT in the table linked above) can be connected via data, terminals, or process I/O, while the setpoint of the subsequent PID (refer to SET in the table linked above) can only be connected via terminals; thus, this connection is of the OUT-SET type.
Reply #72018-01-11
Oh, with that distinction, it makes sense. Thank you! ~

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.