Liquid level measurement of liquid chlorine storage tanks

2018-10-15View Original

Thread Content

For measuring the liquid level in liquid chlorine storage tanks, radar level gauges are used; over time, the readings of these gauges become inaccurate (compared to the local level gauges on site). After recalibration, they function properly. Are there any other methods or approaches for measurement?
Reply #22018-10-16
A corrosion-resistant magnetostrictive level gauge is used; both the measuring rod and the float are made of 316 + PTFE. It provides a 4-20mA output, with either on-site display or RS485 connectivity available.
Reply #32018-10-16
It’s a good approach; the temperature of liquid chlorine is relatively low. Can polytetrafluoroethylene material be used over the long term?
Reply #42018-10-16
PTFE material can be used for a long time; the PTFE we use can withstand temperatures as low as -200°C. The waveguide wire in magnetostrictive level gauges can withstand temperatures of -40°C, and the lowest temperature of liquid chlorine is not lower than -40°C; therefore, magnetostrictive level gauges can operate properly.
Reply #52018-10-16
Our company uses both radio frequency admittance and double flange methods
Reply #62018-10-17
There shouldn’t be any major problems with liquid ammonia radar measurements; please check the radar configuration carefully
Reply #72018-10-17
Learned*: victory:
Reply #82018-10-17
Dual flanges are a better choice; the radar serves as a supplementary element. If only one is to be installed, dual flanges should be given priority. Given the relatively high liquid level range, magnetostrictive and radio frequency admittance measurement rods should not be too long; it is better to use several of them instead.
Reply #92018-10-17
Checked the configuration settings; no issues found
Reply #102018-10-17
There’s a chance to give double flanges a try and see how it goes :)

Submit a Project

**Looking for Chemical Technology, Equipment & Solutions?** No Registration Required Broader Platform Exposure | Global Chemical Service Provider Connections

Submit Request — Free Consultation

Disclaimer

This is an automated machine translation of the original thread. Some technical terms may have inaccuracies; the original text shall prevail. Click "View Original" at the top right to access the source page, which supports IP-based automatic real-time language translation. Please watch out for contact details and sales inducements to prevent fraud. All content and translations are for reference only, representing solely the poster's personal views. For enquiries, email service@hcbbs.com.